I installed myself. On the other side of the wall I put the inlet. Installed 50 amp breaker and connected the transfer switch. Extended 9 circuits from the main breaker to the Generac. It has 8 slots but can accommodate two tandem breakers. Luckily I had 2 breakers that were not arc fault so was able to combine them on the tandem. Basically moved Kitchen, Garage, Family Room, Master Bedroom, and the circuit with the network equipment. Also moved the downstairs furnace to the switch just in case we get another cold snap here in Texas.
The Generac was 339 plus the inlet was 50, generator cable 79, and the romex and breakers needed. Total cost was between 500 and 600.
The transfer switch cuts the hots and neutral so when on generator, it is separate from house neutral preventing a ground fault in the truck.
I am now leaning towards following the same route and doing it myself. This was a good video to watch although he did make some changes that were detailed in the description and comments after the video was uploaded.

Sponsored

 

BlackCloud

Well-known member
First Name
Wayne
Joined
Mar 28, 2021
Threads
3
Messages
68
Reaction score
83
Location
Phoenix / Seattle
Vehicles
2021 KR PowerBoost
Occupation
Retired
For many years I have been running a Honda EM5000S generator to power the house whenever the grid power goes out. This does not happen very often, and when it does, it is seldom for more than a few hours. However, even that short time would be disastrous to the salt water reef tank I have, which requires extremely stable temperature control - hence the backup system.

Ford F-150 Installed Transfer Switch in House IMG_1217


I connect the generator through a GenTran transfer switch box, which allows me to select up to 6 circuits in the house, including the furnace, refrigerator, and aquarium circuits.

Ford F-150 Installed Transfer Switch in House IMG_1184


This weekend was the first chance I had to see if it would work with the PowerBoost Pro Power in place of the Honda generator. Of course, as expected, it immediately tripped the Pro Power off. Now I need to rethink my entire home power setup. That's ok, though. I needed to update the entire panel system anyway.

I just thought I would add my two-bits to this most excellent thread, and confirm once more that the bonded ground issue does not allow the truck be a plug 'n play replacement for a typical generator setup.
 

Ajzride

Well-known member
First Name
Alan
Joined
Jun 6, 2021
Threads
15
Messages
851
Reaction score
1,068
Location
Houston
Vehicles
21Mach-E / 65Mustang / 21PB 502A 157"
Occupation
C&A
Hopefully an electrician or electrical engineer can shed some light for me. I understand why it is an issue, what I don’t understand is why Ford designed it that way. If most generators have a dedicated plug that is unbonded for plugging into a transfer switch, why didn’t they add one to the powerboost? Could the bond be made with a toggle so it could be bonded for worksites and unbonded for transfer switch?
 

UGADawg96

Well-known member
Joined
Feb 28, 2021
Threads
24
Messages
2,731
Reaction score
4,533
Location
JAX, FL
Vehicles
'21 302A 157 PB
For many years I have been running a Honda EM5000S generator to power the house whenever the grid power goes out. This does not happen very often, and when it does, it is seldom for more than a few hours. However, even that short time would be disastrous to the salt water reef tank I have, which requires extremely stable temperature control - hence the backup system.

IMG_1217.jpeg


I connect the generator through a GenTran transfer switch box, which allows me to select up to 6 circuits in the house, including the furnace, refrigerator, and aquarium circuits.

IMG_1184.jpeg


This weekend was the first chance I had to see if it would work with the PowerBoost Pro Power in place of the Honda generator. Of course, as expected, it immediately tripped the Pro Power off. Now I need to rethink my entire home power setup. That's ok, though. I needed to update the entire panel system anyway.

I just thought I would add my two-bits to this most excellent thread, and confirm once more that the bonded ground issue does not allow the truck be a plug 'n play replacement for a typical generator setup.
The reason the Honda EM5000S works with the GenTran is because it is not neutral bonded. You would just need to swap out your GenTran for the Generac and it would work with the PB.

https://powerequipment.honda.com/generators/models/em5000#Specs

Ford F-150 Installed Transfer Switch in House 1627299443551
 

UGADawg96

Well-known member
Joined
Feb 28, 2021
Threads
24
Messages
2,731
Reaction score
4,533
Location
JAX, FL
Vehicles
'21 302A 157 PB
Hopefully an electrician or electrical engineer can shed some light for me. I understand why it is an issue, what I don’t understand is why Ford designed it that way. If most generators have a dedicated plug that is unbonded for plugging into a transfer switch, why didn’t they add one to the powerboost? Could the bond be made with a toggle so it could be bonded for worksites and unbonded for transfer switch?
They did it to comply with code. The truck isn't designed or marketed as a whole house backup generator.
 

Sponsored

kizzle_wizzle

New member
First Name
Keith
Joined
Jul 26, 2021
Threads
0
Messages
3
Reaction score
8
Location
Orlando, Florida
Vehicles
'21 F-150 Lariat PB, '13 Mustang GT
In regards to the "interlock method" a lot has been said about how disconnecting the ground wire between the panel and the PB generator isn't up to code. While I believe that is true, there has to be a reason. I'm just struggling to figure out what that reason is.

Something to consider that I keep going back to in my mind is this: There are just 3 wires that connect the main panel to the utility power. Two hot, and one neutral. The ground in the panel comes from a ground rod driven into the ground near where the utility power enters the building and is not tied to the utility service. Removing the ground wire connection to the PB generator doesn't change this basic configuration. Still the same 3 wires connected to the panel.

Using the "interlock method" and leaving the ground wire disconnected between the truck and the building seems just like using the utility power, only the hot wires are coming into the building from the PB generator and the neutral of the PB generator is tied into the panel to allow the current to "return to the source." All grounding protection and all GFCI outlets in the house should still function the same as the ground still provides a path back to the PB generator neutral since they are bonded at the panel. This is seems exactly how normal utility power and the building electrical systems are designed to work.

I understand following the code is always the best route, but in this case it involves a special transfer switch that limits the number of circuits in the building you can power. Hence why I'm trying to determine the reason the code is the way it is. Does anyone have a full example of how this is unsafe or could cause a problem that the existing electrical infrastructure in the building will not protect from?
 

Hullguy

Well-known member
First Name
Jim
Joined
Oct 14, 2020
Threads
6
Messages
378
Reaction score
362
Location
Weymouth, MA
Vehicles
2013 F150 FX 4
Occupation
Retired Union Electrician
In regards to the "interlock method" a lot has been said about how disconnecting the ground wire between the panel and the PB generator isn't up to code. While I believe that is true, there has to be a reason. I'm just struggling to figure out what that reason is.

Something to consider that I keep going back to in my mind is this: There are just 3 wires that connect the main panel to the utility power. Two hot, and one neutral. The ground in the panel comes from a ground rod driven into the ground near where the utility power enters the building and is not tied to the utility service. Removing the ground wire connection to the PB generator doesn't change this basic configuration. Still the same 3 wires connected to the panel.

Using the "interlock method" and leaving the ground wire disconnected between the truck and the building seems just like using the utility power, only the hot wires are coming into the building from the PB generator and the neutral of the PB generator is tied into the panel to allow the current to "return to the source." All grounding protection and all GFCI outlets in the house should still function the same as the ground still provides a path back to the PB generator neutral since they are bonded at the panel. This is seems exactly how normal utility power and the building electrical systems are designed to work.

I understand following the code is always the best route, but in this case it involves a special transfer switch that limits the number of circuits in the building you can power. Hence why I'm trying to determine the reason the code is the way it is. Does anyone have a full example of how this is unsafe or could cause a problem that the existing electrical infrastructure in the building will not protect from?
The utility drives a ground rod at the transformer. We use the natural conductivity of the “ground” as the 4th wire
 

redactedAlias

Member
Joined
Jun 19, 2021
Threads
3
Messages
22
Reaction score
14
Location
Jacksonville, FL
Vehicles
21 powerboost platinum, 18 road king special
Ughhh! I have contacted every electrician in my area. I never mentioned the truck, only that I needed my home set up for a neutral bonded generator we purchased for hurricane season. 90% had no idea what I meant. One came out to look, said theyd to research on the neutral bonded issue, then called back and said they werent interested. The last said they would do it, and to go get a reliance transfer switch from lowes. Nowhere sells the neutral bonded X series. Not lowes, home depot, ace, tractor supply etc. The generac mentioned in this thread is out of stock too. Hurricane season is supposed to be bad this year and I really want to get this set up for my family. Has ANYONE come up with a safe solution? I mean Ford advertised doing this in the Gulf before the trucks were sold, how did they do it?!
 

jeffcrum

Well-known member
First Name
Jeff
Joined
Feb 21, 2021
Threads
2
Messages
625
Reaction score
670
Location
Lake Saint Louis, MO
Vehicles
2021 F-150 XLT 302A Powerboost 7.2kw Inverter
Occupation
Computer programmer

TBizz

Member
First Name
Thomas
Joined
Nov 16, 2020
Threads
0
Messages
9
Reaction score
10
Location
texas
Vehicles
2014 WK2 Jeep
Occupation
Architect
Any thoughts on how far the transfer switch can be from the main breaker panel? Mine is on the opposite corner of the house from my garage so I’d need a 150’ extension chord or move the switch panel closer to the truck.
 

Sponsored


UGADawg96

Well-known member
Joined
Feb 28, 2021
Threads
24
Messages
2,731
Reaction score
4,533
Location
JAX, FL
Vehicles
'21 302A 157 PB
Ughhh! I have contacted every electrician in my area. I never mentioned the truck, only that I needed my home set up for a neutral bonded generator we purchased for hurricane season. 90% had no idea what I meant. One came out to look, said theyd to research on the neutral bonded issue, then called back and said they werent interested. The last said they would do it, and to go get a reliance transfer switch from lowes. Nowhere sells the neutral bonded X series. Not lowes, home depot, ace, tractor supply etc. The generac mentioned in this thread is out of stock too. Hurricane season is supposed to be bad this year and I really want to get this set up for my family. Has ANYONE come up with a safe solution? I mean Ford advertised doing this in the Gulf before the trucks were sold, how did they do it?!
yeah, I'm in JAX too and have had the same experience. I'm thinking about bailing on the transfer switch idea for now and just running 6/3 for a 50amp TT plug myself.
 

Briansk12

Well-known member
First Name
Brian
Joined
Jul 5, 2021
Threads
4
Messages
63
Reaction score
121
Location
Houston
Vehicles
2021 F-150 PowerBoost
I installed the Generac 6852 about a month ago. Works great. I see a few places online that say they have them. They should run around $339
 

Hullguy

Well-known member
First Name
Jim
Joined
Oct 14, 2020
Threads
6
Messages
378
Reaction score
362
Location
Weymouth, MA
Vehicles
2013 F150 FX 4
Occupation
Retired Union Electrician
Any thoughts on how far the transfer switch can be from the main breaker panel? Mine is on the opposite corner of the house from my garage so I’d need a 150’ extension chord or move the switch panel closer to the truck.
Distance doesn’t matter. The cost of extending the circuits might cause you to gag. It’s $120 for a roll of 14/2 romex in Massachusetts
 

redactedAlias

Member
Joined
Jun 19, 2021
Threads
3
Messages
22
Reaction score
14
Location
Jacksonville, FL
Vehicles
21 powerboost platinum, 18 road king special
yeah, I'm in JAX too and have had the same experience. I'm thinking about bailing on the transfer switch idea for now and just running 6/3 for a 50amp TT plug myself.
I found a small business (father and son) that do a lot of the tesla and such down here in PVB. I really wanted to grab something from a store in case of manufacturing issues, but I was able to get the generac from power equipment something something on the web. Give me a week or two to have them install it and I'll let you know how it goes/who did it.