Re: the neutral-ground bonding in the truck: Ford chose to set up the truck for contractors working at a site without utility power. The neutral-ground bonding is a requirement of OSHA not the NEC. Opening the ground wire between the house and the truck does allow the truck's system to power the house because it no longer senses the neutral-ground bonding in the house. However, this then leaves the truck frame & components without a path to ground. I believe that is a bad, bad idea even if it seems to work. I also believe it is not NEC compliant.
The neutral switching panel discussed above is effectively a means of opening up the neutral-ground bonding in the house. It leaves the ground path for both the truck and the house intact. However these appear to set you up with an "emergency" panel that limits powered house circuits. The 7.2 kW generator in the truck has all the power you need for the full house.
Recall there are four things needed to be safe and compliant with the NEC: 1- an interlock between the generator input and the utility line input; 2- a house input cable box that has a male connection; 3- not using a male-male cable from generator to house (which is why you need #2); and 4- a 4 wire cable connecting the generator to the house of sufficient rating for the generator (eg two hots, 1 neutral and 1 ground wire).
The neutral switching panel discussed above is effectively a means of opening up the neutral-ground bonding in the house. It leaves the ground path for both the truck and the house intact. However these appear to set you up with an "emergency" panel that limits powered house circuits. The 7.2 kW generator in the truck has all the power you need for the full house.
Recall there are four things needed to be safe and compliant with the NEC: 1- an interlock between the generator input and the utility line input; 2- a house input cable box that has a male connection; 3- not using a male-male cable from generator to house (which is why you need #2); and 4- a 4 wire cable connecting the generator to the house of sufficient rating for the generator (eg two hots, 1 neutral and 1 ground wire).